Slashdot Mirror


Facebook Putting Batteries On-Board Its Servers

1sockchuck writes "The data center of the future may have no central UPS units, and be filled with servers with on-board batteries. Facebook says it will adopt a new power distribution design that shifts the UPS and battery backup functions from the data center into the cabinet by adding a 12-volt battery to each server power supply, an approach pioneered by Google. Facebook says the move will slash its power bill and save millions in capital expenses on UPS systems and PDUs. Facebook acknowledged that these types of custom designs are limited to large companies, but called on server vendors and data center builders to adapt their offerings to make them available to smaller companies."

2 of 155 comments (clear)

  1. Re:12 Volt? by TheKidWho · · Score: 4, Informative

    Since when is 12 Volts a measure of battery life? You still need to know how many Amp-Hours the battery can provide and the power usage of the server.

    You could have a 100Amp-Hour 12 volt battery, or a 1Amp-Hour 12 volt battery...

  2. Re:On board batteries fine, but 277 volt? by Cassini2 · · Score: 5, Informative

    277 (V) corresponds to the line to neutral voltage of a 480 (V), 4 wire power distribution system. 480 (V) systems are fairly common in industrial settings in the United States. The major disadvantage of using 480 (V) to power a server, is you can't use a UPS. UPS on 480 (V) systems are rare and expensive, hence the reason why Facebook wants the batteries inside the server.

    I'm pretty certain you really don't want to run servers from the 277 (V) line to neutral voltage of a 480 (V), 4 wire system (3 lives, one neutral). On a 4 wire system, you have 4 wires and you can lose any one of them. If you lose the neutral, your servers could be running of 480 (V) instead of 277 (V). They will be destroyed.

    Losing the neutral is a relatively common failure in 3 phase systems, as many 3 phase systems are 3 phase, 3 wire with a fake neutral/ground connection that is often mistaken for a neutral. This central connection is purely to prevent the 3-wire system from drifting off of off ground, like when lightening strikes, which is common in a big high-voltage system. When operating a 10,000 (V) to 480 (V) step down transformer (the transformers inside the metal fenced enclosures), a small amount of electric slippage to occur between the windings. 1% of 10,000 (V) is 100 (V). Faults can also occur in big loads, like motors. A 10% ground fault on a 480 (V) 400 (A) motor, could be 200 (V) at 40 (A). These voltages/powers are nothing for a 480 (V) motor, but are enough to cause significant damage in a computer with a 1.2 (V) processor. This mismatch is why you should never trust the ground/neutral connection on a high-voltage supply line. It is for safety, not for powering computer equipment, electronic equipment, and electronic motor drives. After having replaced tens of thousands of dollars of electronic motor drives, my rule is: make the supply 480 (V) 4 wire, and all the loads 480 (V) 3 wire. A 3 wire load with no neutral can withstand problems with the neutral. A 4-wire load powering electronics line-to-neutral will not withstand neutral failures.

    If you are going to use 480 (V), you really want to use 480 (V) 3 wire AC (3 live wires, no neutral). If any one power circuit is lost, nothing really bad happens. Also, power semiconductors are readily available for 480 (V), because all the industrial motor drives require them. As such, your power supply will be cheaper.