Insurance Claims Reveal Hidden Electronic Damage From Geomagnetic Storms

KentuckyFC writes: On 13 March 1989, a powerful geomagnetic storm severely disrupted the Hydro-Québec high-voltage grid triggering numerous circuit breakers and blacking out much of eastern Canada and the northeastern U.S. Since then, Earth has been hit by numerous solar maelstroms without such large-scale disruption. But the smaller-scale effect of these storms on low voltage transmissions lines, and the equipment connected to them, has been unknown. Until now. Researchers from the Lockheed Martin Solar and Astrophysics Laboratory have analyzed insurance claims for damage to industrial electrical equipment between 2000 and 2010 and found a clear correlation with geomagnetic activity. They say that the number of claims increases by up to 20 per cent on the days of highest geomagnetic activity. On this basis, they calculate that the economic impact of geomagnetic damage must amount to several billion dollars per year. That raises the question of the impact these storms have on household electronic equipment, such as computers, smartphones and tablets, and whether domestic insurance claims might throw some light on the issue.

13 of 78 comments (clear)

  1. Deductible by Himmy32 · · Score: 3, Insightful

    Probably the damages are below the cost of a homeowner/renters deductible. Lot's of difference between making a claim on a $30 microwave and a $20,000 piece of industrial equipment. Even more so the correlation would probably not be a tight as consumers probably would have a much larger standard deviation on time between equipment failure and when the claim was filed.

  2. Buy Surge Protectors by Virtucon · · Score: 3, Interesting

    If you haven't already bought them, buy surge protectors. After replacing the fourth dishwasher in our less than 8 year old house due to circuitry issues we installed a whole house surge protector. They work and it doesn't take a magnetic storm to cause issues, most of the grid delivery is +/- 15% on voltage just in my area normally.

    --
    Harrison's Postulate - "For every action there is an equal and opposite criticism"
    1. Re:Buy Surge Protectors by Himmy32 · · Score: 4, Insightful

      Not to be pedantic, but people probably would want power conditioners not surge protectors to guard against those conditions. Surge protectors are built to prevent voltage spikes where power conditioners are built to deal with brown-outs and "overvoltage" generally along with spikes.

    2. Re:Buy Surge Protectors by Lumpy · · Score: 4, Interesting

      99% of the surge suppressors you can buy at stores are useless crap that simply use a $0.29 MOV to shunt a voltage spike. they will do NOTHING to stop most real problems that come in on data lines and NOT power. Those things are designed to stop surges from your vacuum cleaner, your furnace and AC, and the industrial building down the street.

      We have customers whine every thunderstorm asking why did their $9.95 surge suppressor not stop lightning damage... It cant, in fact you can not buy anything on this planet that can stop a close or direct lightning hit.

      I have seen lightning blow up electronics that were unplugged and sitting in the cardboard box. getting a hard strike 8 feet from the south wall where all the gear was going to be installed. Every single device was fried when we opened the boxes and hooked it up.

      --
      Do not look at laser with remaining good eye.
    3. Re:Buy Surge Protectors by Anonymous Coward · · Score: 5, Insightful

      It cant, in fact you can not buy anything on this planet that can stop a close or direct lightning hit.

      I have seen lightning blow up electronics that were unplugged and sitting in the cardboard box. getting a hard strike 8 feet from the south wall where all the gear was going to be installed. Every single device was fried when we opened the boxes and hooked it up.

      Wrong. How do commercial antenna located on towers and other locations that are prime targets for large and small strikes survive at all? The CN Tower in Toronto, Canada has an average of 75 strikes a year. Any commercial radio station in Florida would be bankrupt if they lost their transmitters after every time their antennas were hit.

      Just because you don't know how to do it, doesn't make it impossible.

    4. Re:Buy Surge Protectors by SuricouRaven · · Score: 4, Interesting

      I've done that on a small scale, building a can-crusher. It puts out such powerful magnetic field it's like a mini-EMP - at close range it disrupts recording equipment. Camera electronics crash.

    5. Re:Buy Surge Protectors by sjames · · Score: 3, Interesting

      Overstated, not wrong. There's nothing you can buy for the home that won't cost several times more money than the equipment being protected.

      You can buy arresters that will protect against near misses, but if a bolt of lightning hits the outdoor antenna, the TV and arrester will become smoking chunks of plastic and metal.

  3. Look somewhere else by Brit_in_the_USA · · Score: 4, Insightful

    Then look in the sales numbers for replacement appliances and computer pars form bestbuy, newegg etc.

  4. Tablets? by Anonymous Coward · · Score: 3, Informative

    Geomagnetic storms induce very slow changes (over minutes to several hours) in the magnetic field, hence the induced voltage in electrical circuits is very small unless you have very large loops in the circuits (large, as in miles). A tablet is not going pick up any significant voltage, and would have more induced electric currents by setting on top of an extension cord, or attaching a cover that uses a permanent magnet... or walking by a fridge. There is a small chance maybe something happens if it was plugged in, but today most electronics use a switching power supply that can hand a decent range of voltages, and the mains voltage would have to go way out of spec, and then most likely only damage the power supply. And a lot of those power supplies can work at dual voltage, so if you are on a 110 service, you would need it to spike over 220 V to do damage.

    1. Re:Tablets? by Anonymous Coward · · Score: 3, Interesting

      Let's add some numbers to this. The Carrington Event had a peak change in magnetic field of about 1.5 microteslas. Suppose your table for some reason was 30 cm square and had a hundred turns of wire inside it around the perimeter, giving a total effective area of 9 square meters. In order for that 1.5 microtesla field to induce 1 V in the loop, the magnetic field change would need to happen in about 15 microseconds.... the actual change took hours. Even if it happened in a minute, the induced voltage would be 0.2 microvolts, still assuming your tablet had a huge coil of wire in it. (As opposed to say a 100 mile square loop, because you are looking at ground currents or an distribution system with unusual return path, you would get 600 V then...)

  5. Time to apply science by Technician · · Score: 4, Informative

    Time to apply science to the problem. What is known, what values are involved, and what breaks down.

    Long distance transmission lines have two problems when there is a relatively high atmospheric current. They are long conductors feeding transformers that are not designed to shunt large components of DC resulting in core saturation and high current. This is measurable. The first effect noticed was by the railroad when telegraph relays activated and sometimes burned out.

    The voltage induced current has two components. 1 Some current was due to the current directly into the long wire. 2 Some current was due to ground potential changing due to high current in the ground.

    How to protect? For ground potential issues, simple pairs of wires provide high common mode rejection. This is common with telephone circuits as protection from induced hum and noise from a noisy electrical environment. Overvoltage protection in the form of lightning arresters is the second protection. Most phone loops are relatively short reducing the ground voltage gradient problem to non existant levels. Long distance hops are by Microwave Relay or Fiber Optic, both providing protection from ground gradients and long pick up paths.

    Shrink the scale to inside a home by comparison. All internal house wireing is orders of magnatude shorter than transmission lines, CATV, and phone lines. Small DC capible antennas result in very low current if exposed. The home is generally protected by gutters on the eves, mildly conductive building materials such as wood, brick, etc that are not insulated to very low leakage at high voltages such as the insulatin on transmission lines. Net result is the very small currents are shunted by the building itself. Go up on the roof during a geo storm and see if you have any static electricity issues. Probably not.

    For homeowners, this is a non issue due to the lack of an effective gathering surface properly insulated to collect enough current to cause any damage. The collector is too small and the leakage path to ground is too high.

    --
    The truth shall set you free!
  6. Is this news? by GameboyRMH · · Score: 4, Interesting

    I thought it was common knowledge, ask any admin of a network with 100ft+ lines running between buildings. The gear connected to them often fries when solar flares hit. Sometimes it happens so reliably that they have a procedure to disconnect the lines when a solar flare is coming.

    --
    "When information is power, privacy is freedom" - Jah-Wren Ryel
  7. Solar activity by Charliemopps · · Score: 5, Interesting

    I confirmed the effect of solar activity countrywide myself a few years ago...
    I used to work in the NOC (Network operations center) for a major Telco. The job is pretty strait forward, there's an application that gets alerts from a vast and very diverse set of equipment all across the country and displays "alarms" when they are having problems. There are always alarms, but many are transient and a lot of the equipment will fix itself. Your job is to know what's bad, how bad it is and how to intervene if you need to. A remote in the backwoods of Georgia has a fire alarm... Call the fire department who will break down the door, hose down the equipment and put 10,000 people out of service for a week? Or notice that the same remote has a minor fan alarm thats not on your display because of the severity and know that what really is going on is the fan burned up and you can just send a field tech to replace it.

    Anyways, that jobs a lot like war. Long periods of boredom punctuated by brief periods of terror. 100k people without 911 service wares at you. But in the slow times it's really boring so I was surfing one day and found this:
    http://spaceweather.com/
    It's a NASA website that shows the activity in space around the sun/earth. You can even download spreadsheets of past data.
    This got me thinking so I exported alarm activity on the millions of pieces of equipment I watched for the same time period.
    At first it didn't match up, but then I remembered there are local causes to. So I found some data on electrical storms and subtracted that...
    Tada! I had a perfect graph showing the rise and fall of solar activity that matched nicely with my alarm activity. There were a few anomalies, but I'm not scientist. I could see that the effect was more negligible on our fiber networks, but still there. I attributed this to power fluctuations.

    Excited I ran into my bosses office and told him to look at my charts. He said "That's fantastic! Good work! Really interesting! But useless I'm sad to say..."
    I was baffled...
    "Do you want me to block out the sun? This really is neat, but that's about it. We can't do anything about it."
    I thought about it and finally agreed. It's is neat, but also unavoidable. At best we could use it to put more techs on staff on certain days, but that would be about it. And the fact is, there's ALWAYS someone on call... so, though being interesting, it's also irrelevant. About the most interesting part was that fiber made the issue go away... but we already knew fiber was better in just about all cases. This was just more proof.